  • Air-to-water heat pump

F718

Saunier Duval F.718 on a Genia Air Max heat pump: fan blocked

Verified with sources2 sourcesReviewed Oct 3, 2026
Technician coming? See the 2 steps they must show you
Air-to-water heat pump outdoor unit next to a house
Mueller felixCC BY-SA 4.0Image source

Risk level

Medium

Proceed carefully and stop if the check is unclear.

Urgency

Medium

Quick answer

On the Genia Air Max, F.718 means the outdoor unit fan sends no speed signal after several restarts. Clear snow or leaves from the grilles from outside without opening the unit and, if it returns, call a competent person.

Safety first

Stop and check this first

  • The Genia Air contains flammable R290 refrigerant. Saunier Duval forbids ignition sources such as plug sockets, switches or lamps in the protective area around the outdoor unit. Do not open the casing.

Safe checks you can perform

  • Message on the tower display
  • Snow and leaves at the grilles
  • Fan, connector and board

Leave these tasks to a qualified professional

  • Do not attempt this professional task: Fan test before replacing the motor
  • Do not attempt this professional task: Leak check before opening

What a technician must be able to justify

Technician visit

These are the steps they must carry out and show you. Tick them as they work: if steps are skipped, do not accept a part swap.

These are not instructions for opening or handling the equipment yourself. They are the checks that should support a technical conclusion.

  1. Fan test before replacing the motor

    What they doThe competent person runs the fan from the diagnostics menu and checks the connector and signal wiring.

    They must show youthe fan turning in the test and the rpm reading.

    In writingwhat was measured, what was replaced and why.

  2. Leak check before opening

    What they doBefore opening the outdoor unit, the competent person checks with an R290 rated gas detector that there is no leak.

    They must show youthe detector used and its no leak reading.

    In writingthe leak check and the final test with no F.718.

Before accepting a part or repair

Nothing has been shown yet. Do not accept a part swap based on the code alone.

Follow these steps

Note: Follow the documented order. An error code identifies the affected system, but it does not prove by itself which part has failed.

  1. Message on the tower display

    No special tools

    Who:
    you.
    How:
    read the display and note whether it shows F.718, F.785 or status S.252.
    Result that matters:
    S.252 is the automatic restart every 15 minutes; F.718 is the lockout after four attempts.
    If you only see S.252:
    the unit is still retrying; watch whether it reaches F.718.
    If you see F.718 or F.785:
    fan 1 or fan 2 did not start; check the air path.
    Evidence to keep:
    a photo of the display with date and time.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

  2. Snow and leaves at the grilles

    No special tools

    Who:
    you, from outside.
    How:
    remove snow from the air inlet and outlet grilles and leaves gathered around the unit, as the manufacturer lists in product care. Do not push anything between the blades.
    Result that matters:
    that the grilles are clear and no ice is holding the fan.
    If there was a blockage and the code does not return:
    the blockage was the likely cause.
    If there was nothing or the code returns:
    a visible blockage is ruled out; call a competent person.
    Evidence to keep:
    photos of the grilles before and after.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

  3. Fan, connector and board

    Tools required

    Who:
    a competent person.
    How:
    after checking with a gas detector that there is no R290 leak, they open the unit, inspect the fan motor, connector and speed signal, and run the fan from the diagnostics menu.
    Result that matters:
    whether the fan turns when commanded and whether the board reads its rpm.
    If it does not turn with a clear path:
    a motor or supply fault is confirmed.
    If it turns and the board reads no rpm:
    the signal cable or the board is the suspect.
    Evidence to keep:
    a job sheet with the test done and the part involved.

    Flammable R290 refrigerant and mains voltage: isolate all poles, wait at least 3 minutes and check for leaks before opening. Competent person only.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

Still not solved

If the error persists, stop here. See what the technician must do and show you.

Where this code applies

A code is meaningful only inside the right product and version context.

Primary scope

System
Heat pumps
Brand
Saunier Duval
Product type
Air-to-water heat pump

Known code variants

  • aroTHERM F.718
  • aroTHERM plus F718
  • Genia Air F.718
  • Genia Air Max F718
  • Saunier Duval F718
  • Vaillant F718

What it means

Saunier Duval explains F.718 as the missing confirmation signal that fan 1 is turning. Status S.252 acts first: with the fan at 0 rpm the heat pump switches off for 15 minutes and restarts; after four failed restarts it shows F.718. The remedy it gives is to check the air duct and remove the blockage. If the path is clear, the fault may be in the motor, the signal cable or the board, and the code does not say which.

Warnings and stop conditions

  • Highsource verified

    The Genia Air contains flammable R290 refrigerant. Saunier Duval forbids ignition sources such as plug sockets, switches or lamps in the protective area around the outdoor unit. Do not open the casing.

    Evidence: Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

Symptoms and causes

Probable causes · in order

  • Blocked air pathCommon

    Snow, ice, leaves or branches stop the blades or cover the grille. It is visible from outside and is the first thing Saunier Duval asks to check.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

  • Motor or speed signalPossible

    With a clear path and a repeated code, the signal is missing because of the motor, its connector or the cable. Only a competent person with the unit open separates them.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00

  • Outside windLess common

    Saunier Duval shows S.287 when wind turns the fan at 50 rpm or more before start. It is a different status from F.718 and does not explain it.

    Evidence: Saunier Duval GeniaSet FW 200-6 y FEW 200-6, instrucciones de funcionamiento, instalación y mantenimiento 0020291590_01 · Saunier Duval Genia Air HA 4-6 a HA 15-6 O B3, instrucciones de la unidad exterior 0020297943_00